View Full Version : HVAC Question. Type B Vent Pipe Clearance


shootermcgavin
01-04-2018, 09:06 AM
I am remodelling my bathroom and thee "Type B Gas vent pipe is running through the room but was framed around. I would like to move that wall as close as possible to the vent pipe to gain some space on the counter top / vanity. Do any of you know what is the code for clearance on that pipe?

Thanks!

CaberTosser
01-04-2018, 10:07 AM
Type B (double wall) is 1" clearance from combustibles, type C (single wall) is 6"

shootermcgavin
01-04-2018, 10:38 AM
Thanks Caber!