My furnace (Trane, 2 stage hi efficiency, installed in 2013) is short cycling.
Initially, when thermostat was calling for heat, the inducer fan was starting for +/-15 seconds and the furnace was shutting off without ignition. After 15-20 attempts and the inducer fan running at high speed the furnace would eventually start and was working OK until thermostat upstairs was satisfied.
I opened it up and the red light on the board was flashing 3 times meaning a pressure switch problem.
Last week I:
Replaced the filter
Checked air intake and exhaust and made sure they are not clogged by ice.
Checked pressure switches pipes for crack blockage etc.
Check pressure switch for continuity. PS was open no continuity.
Loosen up drain lines, sucked some junk and water out of it and turned the furnace on.
After doing all that, the furnace would need 5-6 attempts to start -much less than before and this time the inducer fan was running at a lower speed. Also this time the furnace would start occasionally for a short period and then shutting down. Red light still flashing 3 times.
I just removed the inducer fan and checked it for scale, debris, blockage. Nothing. The fan was clean.
I also removed and cleaned the flame sensor.
Put everything back and the same thing. Furnace is short cycling 5-6 times and then would start and work OK.
Questions:
Is anything else to be done, except replacing pressure switch?
Should I replace both (hi and low) or only the low pressure one.
Where can I buy them here in Calgary?
Initially, when thermostat was calling for heat, the inducer fan was starting for +/-15 seconds and the furnace was shutting off without ignition. After 15-20 attempts and the inducer fan running at high speed the furnace would eventually start and was working OK until thermostat upstairs was satisfied.
I opened it up and the red light on the board was flashing 3 times meaning a pressure switch problem.
Last week I:
Replaced the filter
Checked air intake and exhaust and made sure they are not clogged by ice.
Checked pressure switches pipes for crack blockage etc.
Check pressure switch for continuity. PS was open no continuity.
Loosen up drain lines, sucked some junk and water out of it and turned the furnace on.
After doing all that, the furnace would need 5-6 attempts to start -much less than before and this time the inducer fan was running at a lower speed. Also this time the furnace would start occasionally for a short period and then shutting down. Red light still flashing 3 times.
I just removed the inducer fan and checked it for scale, debris, blockage. Nothing. The fan was clean.
I also removed and cleaned the flame sensor.
Put everything back and the same thing. Furnace is short cycling 5-6 times and then would start and work OK.
Questions:
Is anything else to be done, except replacing pressure switch?
Should I replace both (hi and low) or only the low pressure one.
Where can I buy them here in Calgary?