Any electricians
I am looking for info on sizing a generator for a small sawmill
I need to run a 30-40 hp 3 phase motor and a couple 5 hp 3 phase plus 7-10kwatts of 110 power Sent from my iPhone using Tapatalk |
I’m a little out of my lane here as I work on the high voltage side, but since no one has responded, I’ll try.
50kva should run the load, just don’t know if it will start the big motor. I’ve seen fairly large gennies trip off on large grain bin aeration fans because of inrush current, even though the unit was rated higher than the running load. See if you can find out from the generator manufacturer what the unit you’re looking at will start. Probably need nameplate data from the motors. Utility power, 50kva would be enough, although it would most likely be installed as a 75kva bank. |
Are you using VFDs for any of the motors?
|
No vfds being used
And yes, inrush current is an issue I was wondering about. Motors will not be started under load... Sent from my iPhone using Tapatalk |
Get a 100 KW genny
|
Can they start together?. We size 3x motor load rating, plus other loads for basic industrial. You could probably get away with the 100kva
|
Ain't going to be cheap. May aswell get line power. The diesel or gas will be ridiculous. 3 phase genny are not cheap
|