pa_of_6 12-10-2019 05:47 PM

Any electricians
 
I am looking for info on sizing a generator for a small sawmill

I need to run a 30-40 hp 3 phase motor and a couple 5 hp 3 phase plus 7-10kwatts of 110 power



Sent from my iPhone using Tapatalk

Opalsasquatch 12-10-2019 06:55 PM

I’m a little out of my lane here as I work on the high voltage side, but since no one has responded, I’ll try.

50kva should run the load, just don’t know if it will start the big motor. I’ve seen fairly large gennies trip off on large grain bin aeration fans because of inrush current, even though the unit was rated higher than the running load.

See if you can find out from the generator manufacturer what the unit you’re looking at will start. Probably need nameplate data from the motors.

Utility power, 50kva would be enough, although it would most likely be installed as a 75kva bank.

Hooter 12-10-2019 07:47 PM

Are you using VFDs for any of the motors?

pa_of_6 12-10-2019 08:19 PM

No vfds being used
And yes, inrush current is an issue I was wondering about. Motors will not be started under load...


Sent from my iPhone using Tapatalk

Dick284 12-10-2019 08:44 PM

Get a 100 KW genny

MyAlberta 12-10-2019 09:50 PM

Can they start together?. We size 3x motor load rating, plus other loads for basic industrial. You could probably get away with the 100kva

trophybook 12-10-2019 11:31 PM

Ain't going to be cheap. May aswell get line power. The diesel or gas will be ridiculous. 3 phase genny are not cheap