I have a REznor unit heater that won't ignite in my garage.

I changed the diaphram and the venter motor. The venter motor was shot, the old one didn't turn on at all.

But it still doesn't ignite. The green light in the board blinks non stop calling for heat and the starts blinking twice.

WHat else could it be?
not familier with that heater,but most gas units sequence of operation start with call for heat,combustion blower starts,pressure switch proves ,pilot(or )ignitor)fires ,proves pilot,main flame ignition.Because you have a led light blinking twice ,that is a code for a problem I would say,check the manual for what that indicates.These are somewhat general instructions so good luck.if you post the model # I can look the manual and get a better idea what kind of heater it is.