Originally Posted by fishunter327 View Post
not familier with that heater,but most gas units sequence of operation start with call for heat,combustion blower starts,pressure switch proves ,pilot(or )ignitor)fires ,proves pilot,main flame ignition.Because you have a led light blinking twice ,that is a code for a problem I would say,check the manual for what that indicates.These are somewhat general instructions so good luck.if you post the model # I can look the manual and get a better idea what kind of heater it is.
Two lights means pressure switch didn't prove. It never clicks.


If it isn't the venter motor or pressure switch, I don't know what it could be?