Default Help need a Plumber

I'm looking for a plumber for my in floor heating system on my house, I'm between Devon and Spruce Grove just west of Edmonton.
I have used one Plumber from Spruce Grove but they come in do a few tweeks charge a couple hundred buck and leave a Month later the problem comes back. I don't think they now what they are doing with this system.
Want someone who is familiar with boilers as now its making a funny noise and the pressure relief valve that the last guy changed is leaking.
Looking for someone reliable that wont rape me on price to do nothing.

Last edited by alpineman; 01-19-2013 at 10:13 AM.
Reply With Quote
  #2  
Old 01-19-2013, 10:47 AM
CaberTosser's Avatar
CaberTosser CaberTosser is offline
 
Join Date: Aug 2007
Location: Calgary
Posts: 19,420
Default

If you're blowing the pressure relief valve there are a few possible causes:

1: You're running too high a system pressure (system should operate no higher than 2/3 of the relief valves pressure rating)

2: Your system expansion tank has insufficient pressure and isn't compensating for system fluid expansion when its heated (its internal bladder could be broken, or in the case of an older open tank it has simply become waterlogged)

3: Insufficient circulation causing excess temperature rise at heat exchanger(possibly failing circ pump(s), plugged system strainer, failed zone valves, failed pressure bypass, scaled heat exchanger, etc)



Based on your 'funny noise' description I might lean towards a circ pump as a prime suspect.
__________________
"The trouble with people idiot-proofing things, is the resulting evolution of the idiot." Me
Reply With Quote
  #3  
Old 01-19-2013, 11:18 AM
CaberTosser's Avatar
CaberTosser CaberTosser is offline
 
Join Date: Aug 2007
Location: Calgary
Posts: 19,420
Default

Another possibility is that your system feeder/pressure reducing valve may be leaking and introducing excessive pressure to your system. Hopefully your pressure guages are accurate, what readings are you getting?
__________________
"The trouble with people idiot-proofing things, is the resulting evolution of the idiot." Me
Reply With Quote
  #4  
Old 01-19-2013, 11:27 AM
alpineman's Avatar
alpineman alpineman is offline
 
Join Date: Aug 2008
Location: Alberta
Posts: 350
Default

Ya i'm thinking it might be the circ pump just not real familliar with the system will need to have someone take a look at it.
The heating system is a Heat Link and the boiler is a Super Hot Saturn Series here is a pic of what I think is the Circ pump its what is starting to make noise.

photo1.jpg
Reply With Quote
  #5  
Old 01-19-2013, 11:36 AM
alpineman's Avatar
alpineman alpineman is offline
 
Join Date: Aug 2008
Location: Alberta
Posts: 350
Default

Quote:
Originally Posted by CaberTosser View Post
Another possibility is that your system feeder/pressure reducing valve may be leaking and introducing excessive pressure to your system. Hopefully your pressure guages are accurate, what readings are you getting?
When I checked it earlier this morning it was showing 0 PSI I added water to it and now when its heating its showing about 15 PSI at 120F
Reply With Quote
  #6  
Old 01-19-2013, 11:41 AM
alpineman's Avatar
alpineman alpineman is offline
 
Join Date: Aug 2008
Location: Alberta
Posts: 350
Default

I'm also thinking he put to small of a pressure relief valve on as when I add water to the system it blows real easy and continues to dribble out after. Thats where I'm loosing fluid.
Its so bad that this morning the system stopped working til I added water to it.
Reply With Quote
  #7  
Old 01-19-2013, 11:55 AM
Stu Stu is offline
 
Join Date: Apr 2010
Posts: 105
Default Improper pump orientation

Shaft should be horizontal.
Probably no flow.
Reply With Quote
  #8  
Old 01-19-2013, 12:15 PM
Elk Hunter17's Avatar
Elk Hunter17 Elk Hunter17 is offline
 
Join Date: Dec 2009
Location: Edmonton
Posts: 366
Default

We use parkland heating and ac, they've been good for us.
Reply With Quote
  #9  
Old 01-19-2013, 12:41 PM
alpineman's Avatar
alpineman alpineman is offline
 
Join Date: Aug 2008
Location: Alberta
Posts: 350
Default

Quote:
Originally Posted by Elk Hunter17 View Post
We use parkland heating and ac, they've been good for us.
Thanks Elk Hunter
Reply With Quote
  #10  
Old 01-19-2013, 12:45 PM
billie billie is offline
 
Join Date: Aug 2010
Location: Rural Calgary
Posts: 1,376
Default

Further to Caber's suggestions, if your expansion tank does not have any air in it, you will get thermal pumping through the pressue relief valve and the symtoms you describe. An easy check is to locate the valve on the tank and ensure you have air or air pressure in it. If it has an internal bladder and you get water, it needs to be replaced (recharged if it has doesn't have a bladder). Newer ones should have air/water separation inside.

Just changed mine in December for the that reason and you don't need a service call, easy to replace. About $140 IIRC, but at a wholesaler which likely aren't open on the weekend.
Reply With Quote
  #11  
Old 01-19-2013, 01:04 PM
CaberTosser's Avatar
CaberTosser CaberTosser is offline
 
Join Date: Aug 2007
Location: Calgary
Posts: 19,420
Default

Quote:
Originally Posted by Stu View Post
Shaft should be horizontal.
Probably no flow.
The motor shaft doesn't have to be horizontal, it just can't be mounted 'motor up' to avoid an air trap in a wet-rotor pump. The pumps disperse their heat into the system fluid, if there's an air trap in the motor housing the motor isn't being cooled, and the motor windings overheat and short circuit. His is 'motor down', so it cannot form an air trap. I always mount with the motor on the horizontal, but that orientation is permitted.
__________________
"The trouble with people idiot-proofing things, is the resulting evolution of the idiot." Me
Reply With Quote
  #12  
Old 01-19-2013, 01:32 PM
alpineman's Avatar
alpineman alpineman is offline
 
Join Date: Aug 2008
Location: Alberta
Posts: 350
Default

Quote:
Originally Posted by billie View Post
Further to Caber's suggestions, if your expansion tank does not have any air in it, you will get thermal pumping through the pressue relief valve and the symtoms you describe. An easy check is to locate the valve on the tank and ensure you have air or air pressure in it. If it has an internal bladder and you get water, it needs to be replaced (recharged if it has doesn't have a bladder). Newer ones should have air/water separation inside.

Just changed mine in December for the that reason and you don't need a service call, easy to replace. About $140 IIRC, but at a wholesaler which likely aren't open on the weekend.
Going to check the Expansion tank Do you know what the air pressure should be at?
Reply With Quote
  #13  
Old 01-19-2013, 01:51 PM
alpineman's Avatar
alpineman alpineman is offline
 
Join Date: Aug 2008
Location: Alberta
Posts: 350
Default

K just checked the Pressure in the tank I'm presuming the blader is shot as liquid is coming out of the air valve it was showing 13PSI on my air pressure gauge. Here are a couple pics of my tank.
Attached Images
File Type: jpg photo.JPG (103.5 KB, 25 views)
File Type: jpg photo 2-1.jpg (31.9 KB, 27 views)
Reply With Quote
  #14  
Old 01-19-2013, 02:05 PM
CaberTosser's Avatar
CaberTosser CaberTosser is offline
 
Join Date: Aug 2007
Location: Calgary
Posts: 19,420
Default

That exp tank is toast for sure. One thing I suggest when replacing it is to put a 1/2" ball valve between the system and the tank, this will allow you to replace it without spilling hot water all over tarnation. Between the shut off valve and the tank put in a tee with a hose valve in the branch; this allows testing of the exp tank. To test an expansion tank you need to isolate it from the system (first ball valve) then drain the fluid through the hose bibb so that your tire pressure gauge you set to the exp tank air chuck reads the bladder air pressure rather than the systems liquid pressure. An expansion tank bladder cannot be checked without bleeding off the systems liquid pressure.
__________________
"The trouble with people idiot-proofing things, is the resulting evolution of the idiot." Me
Reply With Quote
  #15  
Old 01-19-2013, 02:11 PM
pgavey pgavey is offline
 
Join Date: Oct 2009
Location: Beaver Mines AB.
Posts: 881
Default

Had a problem at my shop last winter PR valve blowing of over night and making a mess in the boiler room, Changed out exp tank fixed the problem.
Reply With Quote
  #16  
Old 01-19-2013, 02:15 PM
alpineman's Avatar
alpineman alpineman is offline
 
Join Date: Aug 2008
Location: Alberta
Posts: 350
Default

Quote:
Originally Posted by CaberTosser View Post
That exp tank is toast for sure. One thing I suggest when replacing it is to put a 1/2" ball valve between the system and the tank, this will allow you to replace it without spilling hot water all over tarnation. Between the shut off valve and the tank put in a tee with a hose valve in the branch; this allows testing of the exp tank. To test an expansion tank you need to isolate it from the system (first ball valve) then drain the fluid through the hose bibb so that your tire pressure gauge you set to the exp tank air chuck reads the bladder air pressure rather than the systems liquid pressure. An expansion tank bladder cannot be checked without bleeding off the systems liquid pressure.
Thanks CaberTosser
Wish you were closer I'd hire you to come and check out the system and have a couple beer,
Do you know the best place to pick up a tank on Monday,
Great point on the tee with a hose valve and ball valve I'll defanetly do that.
Reply With Quote
  #17  
Old 01-19-2013, 02:16 PM
Stu Stu is offline
 
Join Date: Apr 2010
Posts: 105
Default

Quote:
Originally Posted by CaberTosser View Post
The motor shaft doesn't have to be horizontal, it just can't be mounted 'motor up' to avoid an air trap in a wet-rotor pump. The pumps disperse their heat into the system fluid, if there's an air trap in the motor housing the motor isn't being cooled, and the motor windings overheat and short circuit. His is 'motor down', so it cannot form an air trap. I always mount with the motor on the horizontal, but that orientation is permitted.

Grundfos doesn't recommend installation in that orientation.
I guess taco's are different.

See page four.
http://ca.grundfos.com/content/dam/G...P%20Series.pdf
Reply With Quote
  #18  
Old 01-19-2013, 02:21 PM
fishunter327's Avatar
fishunter327 fishunter327 is offline
 
Join Date: Oct 2012
Location: 65km south of Stoner
Posts: 644
Default

Not a big fan of Taco.
Reply With Quote
  #19  
Old 01-19-2013, 02:25 PM
alpineman's Avatar
alpineman alpineman is offline
 
Join Date: Aug 2008
Location: Alberta
Posts: 350
Default

Quote:
Originally Posted by Stu View Post
Grundfos doesn't recommend installation in that orientation.
I guess taco's are different.

See page four.
http://ca.grundfos.com/content/dam/G...P%20Series.pdf
So I should change it to be motor horizontal?. Might be a big job as no room where its at.

Should I get another WATTS Tank or what would you guys suggest?
Reply With Quote
  #20  
Old 01-19-2013, 02:25 PM
Stu Stu is offline
 
Join Date: Apr 2010
Posts: 105
Default Taco installation

Not recommended by taco either, but they also say it can be "motor up".
Have a look.
http://www.taco-hvac.com/uploads/Fil...ry/102-054.pdf
Reply With Quote
  #21  
Old 01-19-2013, 02:42 PM
alpineman's Avatar
alpineman alpineman is offline
 
Join Date: Aug 2008
Location: Alberta
Posts: 350
Default

Quote:
Originally Posted by Stu View Post
Not recommended by taco either, but they also say it can be "motor up".
Have a look.
http://www.taco-hvac.com/uploads/Fil...ry/102-054.pdf
After closer look it can be changed to horizontal. the motor is a TACO
Reply With Quote
  #22  
Old 01-19-2013, 03:18 PM
CaberTosser's Avatar
CaberTosser CaberTosser is offline
 
Join Date: Aug 2007
Location: Calgary
Posts: 19,420
Default

These units are good space savers for that suggestion I made regarding an exp tank isolation & bleed assembly:



The left hand port is intended to introduce your system feed from, but you could just screw a 1/2" plug into it.

Stu: I'll have to find which manufacturer had the bottom mount configuration allowed. Its usually the top-mount ones I'm finding with burnt-out motors all the flipping time. I don't think it would have been Armstrong as I don't use them as frequently a Grundfos or Wilo.

Alpine: You could find an expansion tank and one of those valves I linked at Cronkhite or Wolseley in Edmonton.
__________________
"The trouble with people idiot-proofing things, is the resulting evolution of the idiot." Me
Reply With Quote
  #23  
Old 01-19-2013, 04:00 PM
alpineman's Avatar
alpineman alpineman is offline
 
Join Date: Aug 2008
Location: Alberta
Posts: 350
Default

Thanks CaberTosser
Reply With Quote
  #24  
Old 01-19-2013, 04:05 PM
TheLegend TheLegend is offline
Banned
 
Join Date: Mar 2011
Location: FTR Road in the summer (flyfishin), The bush in autum (huntin) the hills in winter (shreddin the pow
Posts: 1,136
Default

Try Forbs mechanical. They do free evaluations and are experienced with boilers.
Reply With Quote
  #25  
Old 01-19-2013, 04:40 PM
CaberTosser's Avatar
CaberTosser CaberTosser is offline
 
Join Date: Aug 2007
Location: Calgary
Posts: 19,420
Default

While I'm always happy to help with advice, it's still a good idea to get a reputable local company to send out a journeyman tech to inspect your system. There also the possibility that you may be suffering from more than one single issue. I always just love the calls where I have to repair one thing in order for it to be possible to troubleshoot any further (repeat trips for parts, anyone? )
__________________
"The trouble with people idiot-proofing things, is the resulting evolution of the idiot." Me
Reply With Quote
  #26  
Old 01-19-2013, 04:51 PM
alpineman's Avatar
alpineman alpineman is offline
 
Join Date: Aug 2008
Location: Alberta
Posts: 350
Default

Quote:
Originally Posted by CaberTosser View Post
While I'm always happy to help with advice, it's still a good idea to get a reputable local company to send out a journeyman tech to inspect your system. There also the possibility that you may be suffering from more than one single issue.
Totally agree and will have someone come and take a look at my system.
Reply With Quote
  #27  
Old 01-19-2013, 04:55 PM
mudbug's Avatar
mudbug mudbug is offline
 
Join Date: Feb 2010
Location: 3rd rock from the sun, formerly from 4th rock from the sun
Posts: 5,000
Smile

Yep I agree with Caber, the tank is toast. Check out Bartle and Gibson in Spruce Grove on Monday, I'm sure they will have one or can get find or get one in a day or so
__________________
I may not be the brightest crayon in the box at times but I sure am colourful
Reply With Quote
  #28  
Old 01-19-2013, 07:36 PM
twofifty twofifty is offline
 
Join Date: Nov 2007
Location: S.E. British Columbia
Posts: 4,579
Default

Caber your plumbing posts are a goldmine of practical diagnostic info. Thx.
Reply With Quote
  #29  
Old 01-19-2013, 07:49 PM
alpineman's Avatar
alpineman alpineman is offline
 
Join Date: Aug 2008
Location: Alberta
Posts: 350
Default

Quote:
Originally Posted by twofifty View Post
Caber your plumbing posts are a goldmine of practical diagnostic info. Thx.
Yes they are can't thank you enought.
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -6. The time now is 05:04 PM.


Powered by vBulletin® Version 3.8.5
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.