Default New Furnace Problem - exhaust icing

Had a new 2-stage furnace installed two years ago. Exhaust pipe goes through the foundation about 2’ above ground and extends about 2’ out. During these cold periods, moisture drips from the end of the exhaust to the ground as it should, but a column of ice builds up (about 3” in diameter. After a regular furnace inspection/filter change it has taken 12 days for the ice column to come within a half an inch of the exhaust pipe. A few more days and it probably starts blocking off the exhaust wth probably CO backup into the house.
So far the installer has offered no solution. Has anyone discovered a way(s) around this that works and can be relied on?
Reply With Quote
  #2  
Old 12-29-2021, 09:47 AM
ganderblaster ganderblaster is offline
 
Join Date: Jan 2010
Location: WMU 226
Posts: 2,198
Default

Mine does that too. Keep an old ax nearby especially in these temps . Give the ice a whack every couple days. Not ideal but it works. Oddly last year was way worse then this one. This year just a small Icicle
__________________
As a man thinketh in his heart so he is
Reply With Quote
  #3  
Old 12-29-2021, 09:53 AM
Twisted Canuck's Avatar
Twisted Canuck Twisted Canuck is offline
 
Join Date: Jul 2009
Location: GP AB
Posts: 16,239
Default

They all do that in cold weather. As mentioned, knock it down with an axe or whatever implement is handy. It's not really a big deal. If it were dangerous, the Code would change in a hurry.
__________________
'Once the monkeys learn they can vote themselves a banana, they'll never climb another tree.'. Robert Heinlein

'You can accomplish a lot more with a kind word and a gun, than with a kind word alone.' Al Capone
Reply With Quote
  #4  
Old 12-29-2021, 10:01 AM
Dean2's Avatar
Dean2 Dean2 is offline
 
Join Date: Dec 2008
Location: Near Edmonton
Posts: 15,049
Default

I knock it off too. One thing, if you let it build up too much, your furnace may refuse to run because it can't vent enough. I have seen that happen to two neighbours last winter.
Reply With Quote
  #5  
Old 12-29-2021, 10:14 AM
fishunter327's Avatar
fishunter327 fishunter327 is offline
 
Join Date: Oct 2012
Location: 65km south of Stoner
Posts: 644
Default

Quote:
Originally Posted by pdog15 View Post
Had a new 2-stage furnace installed two years ago. Exhaust pipe goes through the foundation about 2’ above ground and extends about 2’ out. During these cold periods, moisture drips from the end of the exhaust to the ground as it should, but a column of ice builds up (about 3” in diameter. After a regular furnace inspection/filter change it has taken 12 days for the ice column to come within a half an inch of the exhaust pipe. A few more days and it probably starts blocking off the exhaust wth probably CO backup into the house.
So far the installer has offered no solution. Has anyone discovered a way(s) around this that works and can be relied on?
Is there a 90 deg fitting on the end of the exhaust or does it vent straight out ?
Reply With Quote
  #6  
Old 12-29-2021, 10:43 AM
Big Grey Wolf Big Grey Wolf is offline
 
Join Date: Sep 2012
Posts: 6,266
Default

When you shovel the walk knock it over with your snow shovel, part of 'preventive maintenance' these days.
Reply With Quote
  #7  
Old 12-29-2021, 11:13 AM
Arty Arty is offline
 
Join Date: Jul 2012
Location: one Fort or another
Posts: 768
Default

Considering there's so much infinite and free electricity floating about that some people push cars around with it, just run the plastic pipe into a short section of electrically heated steel pipe. The hot metal should evaporate the few drops of water.

Of course that will consume more energy and materials than the little bit saved by not running a warm stack out through the roof, but such things never bothered the pointy-shoes eco crowd. After all, materials cost nothing and electricity is clean and therefore free.

Alternatively, maybe tee off the exhaust pipe before it punches out the wall so the drops fall down into an inside drain. Sort of like a water trap in a steam line.

Personally, I'd just use an old chunk of 2x4 or axe to smack over the stalagmite when doing the weekly walk-around house inspection. Beats the heck out of what they used to have to do with the frozen mountain under a biffy.
Reply With Quote
  #8  
Old 12-29-2021, 11:19 AM
buckbrush's Avatar
buckbrush buckbrush is offline
 
Join Date: Mar 2008
Posts: 2,073
Default

My wife uses an axe to chip it away once a week or so. I used to do it then she just took over one day. I think she just just likes weilding the axe??

I have had it build up and shut the furnace off a few times over the years. (Pretty sure CaberTosser diagnosed that one for me the first time I woke up to no heat)
Reply With Quote
  #9  
Old 12-29-2021, 11:22 AM
traderal traderal is offline
 
Join Date: Dec 2010
Location: East Central AB
Posts: 1,145
Default

My stacks are on the roof, I climb a ladder and use the long handle from my snow shovel to knock off the ice. If I wasn't around not sure the wife could do it.
Reply With Quote
  #10  
Old 12-29-2021, 11:25 AM
buckbrush's Avatar
buckbrush buckbrush is offline
 
Join Date: Mar 2008
Posts: 2,073
Default

Quote:
Originally Posted by Arty View Post
Beats the heck out of what they used to have to do with the frozen mountain under a biffy.
Ya, I think I would have just added a lift kit to the outhouse...

On That note I once saw a portajohn that had a frozen stalagmite sticking up higher than the seat and the Frac crew had resorted to squatting on the seat to add to it. Probably one of the most disturbing things I've seen in the patch...
Reply With Quote
  #11  
Old 12-29-2021, 11:27 AM
pdog15 pdog15 is offline
 
Join Date: Jun 2013
Posts: 478
Default

Appreciate your thoughts/comments. So far the toe of my work boot has worked ok. Problem would be if the house was vacant for any length of time. Will try a piece of plastic or tin at an angle on the ground to drain the drip away from the exhaust. The exhaust is pretty much parallel to the ground with a slight down slope.
Reply With Quote
  #12  
Old 12-29-2021, 11:35 AM
gunluvr's Avatar
gunluvr gunluvr is offline
 
Join Date: Sep 2012
Posts: 1,598
Default

Quote:
Originally Posted by Arty View Post

Alternatively, maybe tee off the exhaust pipe before it punches out the wall so the drops fall down into an inside drain. Sort of like a water trap in a steam line.
This would be a simple fix.
My neighbor has a big icicle below the exhaust outlet that forms from the ground up. Often, it grows nearly up to the pipe but never quite touches it because the warm air that escapes continuously melts the top of the icicle.
__________________
Some days you're a bullet; some days you're a gopher.
Reply With Quote
  #13  
Old 12-29-2021, 11:54 AM
vinny vinny is offline
 
Join Date: May 2008
Location: The South
Posts: 1,128
Default

Please be extremely careful altering any type of venting. Improper venting or restrictions can cause a very dangerous situation with CO in your home. We get way too many CO calls this time of year. And they don’t all turn out ok. Clearing the ice is the safest method, or at least consult a professional before making any changes.
Reply With Quote
  #14  
Old 12-29-2021, 12:34 PM
58thecat's Avatar
58thecat 58thecat is offline
 
Join Date: Dec 2012
Location: At the end of the Thirsty Beaver Trail, Pinsky lake, Alberta.
Posts: 24,595
Default

Chop the ice down daily, or at least inspect it so nothing goes real bad.


Sent from my iPhone using Tapatalk
__________________

Be careful when you follow the masses, sometimes the "M" is silent...
Reply With Quote
  #15  
Old 12-29-2021, 12:41 PM
Arty Arty is offline
 
Join Date: Jul 2012
Location: one Fort or another
Posts: 768
Default

Quote:
Originally Posted by vinny View Post
Please be extremely careful altering any type of venting. Improper venting or restrictions can cause a very dangerous situation with CO in your home. We get way too many CO calls this time of year. And they don’t all turn out ok. Clearing the ice is the safest method, or at least consult a professional before making any changes.
So would HVAC draining into septic sewer be subject to plumbing code or HVAC code?

Seems to me it would be straight-forward to set up a tee off the fan-driven horizontal (cool) exhaust vent to drain condensate into a standard p-trap setup. Sewer gas is blocked as usual, and CO continues to be driven out the side of the house.

The danger would be not doing anything about ice buildup, thereby blocking exhaust with trace CO amounts from escaping. At least until any protective mechanisms trip the furnace completely.

I'd guess running plastic exhaust vents up an old chimney path would lead to all sorts of problems with condensate flooding and corroding the exhaust fan, so it has to be sent out through a wall. Arguably equally problematic is freezing the exhaust vent shut. I wonder how long it will be before ABC mandates a sewer tie-in for condensate...
Reply With Quote
  #16  
Old 12-29-2021, 12:41 PM
badbrass badbrass is offline
 
Join Date: May 2007
Posts: 1,751
Default

Quote:
Originally Posted by pdog15 View Post
Appreciate your thoughts/comments. So far the toe of my work boot has worked ok. Problem would be if the house was vacant for any length of time. Will try a piece of plastic or tin at an angle on the ground to drain the drip away from the exhaust. The exhaust is pretty much parallel to the ground with a slight down slope.
And that's your problem! I also had a new furnace installed about 5 years ago.
When they are installing the pipes, one cold air and exhaust, i noticed that the pipes had a slight upward slant to them, and asked why they were installing them that way? He said I would thank him someday, as the little bit of moisture would go back into the furnace and not outside. This furnace has a drip pan, and as the furnace burns natural gas, and the moisture for the exhaust, the moisture then goes down a line into the floor drain. That's how they are to work correctly!
I have never had a problem at all with ice build up, or with the furnace!

Last edited by badbrass; 12-29-2021 at 12:50 PM.
Reply With Quote
  #17  
Old 12-29-2021, 01:35 PM
MK2750's Avatar
MK2750 MK2750 is offline
 
Join Date: Mar 2008
Location: Sylvan Lake
Posts: 3,423
Default

The exhaust pipe should be angled no less than 5 degrees towards the furnace. Do not drill any holes in the pipe as any condensation would run back to the furnace anyway.

Straight pipes cause problems. Creating a 90 degree angle up and then another 90 out away from the house is a procedure that generally eliminates a lot of issues. It also eliminates false trip out if a strong gust of wind blows in the pipe.

Code requires an exhaust be off the ground to avoid snow drifting and ice build up. Anything under 2 feet can give issues. The periscope method above helps with that issue as well.

The wrong sized pipe can cause venting issues in extreme cold, consult the installation manual.

Finally, the wrong size furnace can cause issues. Furnaces are more often than not oversized. A furnace that is too large for the duct system looses more heat out the exhaust. One would think this would melt the ice but in fact it moves the condensation process from indoors to outside. If the furnace was putting 95% plus up the duct system the exhaust gases would cool more in and around the furnace and the condensate would run down the drain instead of being blown out the pipe.
Reply With Quote
  #18  
Old 12-29-2021, 02:01 PM
Grizzly Adams1 Grizzly Adams1 is online now
 
Join Date: Sep 2021
Posts: 3,782
Default

Quote:
Originally Posted by vinny View Post
Please be extremely careful altering any type of venting. Improper venting or restrictions can cause a very dangerous situation with CO in your home. We get way too many CO calls this time of year. And they don’t all turn out ok. Clearing the ice is the safest method, or at least consult a professional before making any changes.
X2, that post was a head shaker. That ice build up is normal, just deal with it.

Grizz
__________________
Woe unto them that join house to house, that lay field to field, till there is no place, that they be alone in the midst of the Earth.

Isaiah 5:8
Reply With Quote
  #19  
Old 12-29-2021, 02:03 PM
urban rednek's Avatar
urban rednek urban rednek is offline
 
Join Date: Jul 2016
Posts: 3,422
Exclamation Don't forget

You say the furnace is 2 years old? Best make sure your furnace guy has the following parts available for you: flame sensor, ignitor, and high pressure limit switch.
IIRC- those are the 3 main components the manufacturers use for continual revenue generation.
__________________
“One of the sad signs of our times is that we have demonized those who produce, subsidized those who refuse to produce, and canonized those who complain.” - Thomas Sowell

“We seem to be getting closer and closer to a situation where nobody is responsible for what they did but we are all responsible for what somebody else did.”- Thomas Sowell
Reply With Quote
  #20  
Old 12-29-2021, 04:03 PM
waldedw's Avatar
waldedw waldedw is offline
 
Join Date: Apr 2015
Location: Lloydminster
Posts: 4,506
Default

Mine in the garage does the same thing, it has for the 17 years I have lived here, I just knock it over with my ice scraper for the driveway, no big deal
__________________
The problem we have today is that the people who work for a living are outnumbered by the people who vote for a living.

We were all born ignorant but one must work very hard to remain that way.
Reply With Quote
  #21  
Old 12-29-2021, 04:05 PM
thumper's Avatar
thumper thumper is offline
 
Join Date: May 2007
Location: Canmore
Posts: 4,754
Default

On ours, a little water dripped down, but steam went up, condensing and freezing on the rain gutters and forming huge icicles that pulled the rain gutters off the roof.
We had to re-route the piping in the basement, to lead to the centre of the 'end' of the house where the outlet is well below the house eave.
__________________
The world is changed by your action, not by your opinion.
Reply With Quote
  #22  
Old 12-29-2021, 05:51 PM
Battle Rat Battle Rat is online now
 
Join Date: Dec 2008
Posts: 2,615
Default

Quote:
Originally Posted by pdog15 View Post
Appreciate your thoughts/comments. So far the toe of my work boot has worked ok. Problem would be if the house was vacant for any length of time. Will try a piece of plastic or tin at an angle on the ground to drain the drip away from the exhaust. The exhaust is pretty much parallel to the ground with a slight down slope.
Your solution will need a heat trace if you expect it not to freeze and pile up as it is expelled.
__________________
Thank you front line workers and volunteers
Reply With Quote
  #23  
Old 12-29-2021, 06:25 PM
Cold lake guy Cold lake guy is offline
 
Join Date: Nov 2018
Posts: 70
Default

Journeyman plumber/gasfitter self employed
ALL furnace vents are to be graded 1/4 back towards thee furnace, if you have a single white pipe to the outside you need to snorkel the termination. A 90 straight up then a 6” pipe then a 45 elbow off that a short pipe cut at a 45 angle. Think of an rig exhaust pipe.

No sags in the pipe that will trap water, and again drain the pipe back towards the furnace

No more ice
Reply With Quote
  #24  
Old 12-29-2021, 06:28 PM
Cold lake guy Cold lake guy is offline
 
Join Date: Nov 2018
Posts: 70
Default

Out the roof push a rag in, no plastic fillings inside. Cut at a 45, about 18 above roof line and insulate the pipe in the attic

Remove the rag
Reply With Quote
  #25  
Old 12-29-2021, 06:31 PM
Cold lake guy Cold lake guy is offline
 
Join Date: Nov 2018
Posts: 70
Default

Oh ya put a heat trace on an empty pipe……read the label keep a fire extinguisher handy
Reply With Quote
  #26  
Old 12-30-2021, 11:17 AM
bat119's Avatar
bat119 bat119 is offline
 
Join Date: Jan 2012
Location: On the border in Lloydminster
Posts: 8,364
Default

Time to get the axe out for the shop vent

__________________
Si vis pacem, para bellum
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -6. The time now is 03:28 PM.


Powered by vBulletin® Version 3.8.5
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.