Default question for gas fitters

I set up a mobile this summer with a propane furnace and water heater, and an overhead furnace in the shop(75,000 btu). The journeyman who installed the system ran 1/2" copper to each of the 3 appliances coming off one regulator at the 1000 gallon tank. The regulator is a combination high/low pressure regulator. The contractor who is installing the garage heater says this is wrong, and we need a high pressure reg at the tank and 3 secondary low pressures at the outside of the building. He said we wouldn't have enough propane during cold weather to run the appliances with this setup. Who's right?
Reply With Quote
  #2  
Old 11-11-2014, 08:31 PM
Sashi's Avatar
Sashi Sashi is offline
 
Join Date: Jan 2014
Posts: 1,154
Default

I'm not a gas fitter but have instrument experience. I would go with one high pressure reg at the tank and low pressure regulators at each device.This insures adequate propane volumes for each user. But check with the provider does he guarantee his installation?
__________________
"The further a society drifts from truth, the more it will hate those who speak it."--- George Orwell
There is no way to make something "Idiot Proof" because Idiots are so resourceful.
Reply With Quote
  #3  
Old 11-11-2014, 08:37 PM
357xp's Avatar
357xp 357xp is offline
 
Join Date: Jan 2012
Location: by the crick
Posts: 801
Default

What I would do is first stage reg at tank and second stage at building entrance, run 1 blk pipe in (sized according to total btu's) and branch off at each appliance.
Copper tubing isn't cheap.
As far as legal, what u have should work, depending what size reg u have, how far your runs are and what size each unit is.
Reply With Quote
  #4  
Old 11-11-2014, 08:48 PM
northerntrapper northerntrapper is offline
 
Join Date: Sep 2007
Location: Slave Lake, Alberta
Posts: 386
Default Regs

Okay, thanks. Sounds like the consensus is First stage at the tank, and 2nd stages at the building entrances. Contractor coming in the morning to remove the 2 stage reg. on the tank and refit. Thanks again!
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -6. The time now is 02:39 PM.


Powered by vBulletin® Version 3.8.5
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.