Default Any electricians

I am looking for info on sizing a generator for a small sawmill

I need to run a 30-40 hp 3 phase motor and a couple 5 hp 3 phase plus 7-10kwatts of 110 power



Sent from my iPhone using Tapatalk
Reply With Quote
  #2  
Old 12-10-2019, 06:55 PM
Opalsasquatch's Avatar
Opalsasquatch Opalsasquatch is offline
 
Join Date: Aug 2012
Location: Northeast of Edmonton
Posts: 427
Default

I’m a little out of my lane here as I work on the high voltage side, but since no one has responded, I’ll try.

50kva should run the load, just don’t know if it will start the big motor. I’ve seen fairly large gennies trip off on large grain bin aeration fans because of inrush current, even though the unit was rated higher than the running load.

See if you can find out from the generator manufacturer what the unit you’re looking at will start. Probably need nameplate data from the motors.

Utility power, 50kva would be enough, although it would most likely be installed as a 75kva bank.
Reply With Quote
  #3  
Old 12-10-2019, 07:47 PM
Hooter's Avatar
Hooter Hooter is offline
 
Join Date: Dec 2008
Location: Edmonton
Posts: 958
Default

Are you using VFDs for any of the motors?
Reply With Quote
  #4  
Old 12-10-2019, 08:19 PM
pa_of_6 pa_of_6 is offline
 
Join Date: Oct 2009
Posts: 467
Default

No vfds being used
And yes, inrush current is an issue I was wondering about. Motors will not be started under load...


Sent from my iPhone using Tapatalk
Reply With Quote
  #5  
Old 12-10-2019, 08:44 PM
Dick284's Avatar
Dick284 Dick284 is offline
 
Join Date: May 2007
Location: Dreadful Valley
Posts: 14,585
Default

Get a 100 KW genny
__________________


There are no absolutes
Reply With Quote
  #6  
Old 12-10-2019, 09:50 PM
MyAlberta MyAlberta is offline
 
Join Date: Jul 2017
Posts: 1,417
Default

Can they start together?. We size 3x motor load rating, plus other loads for basic industrial. You could probably get away with the 100kva

Last edited by MyAlberta; 12-10-2019 at 09:56 PM.
Reply With Quote
  #7  
Old 12-10-2019, 11:31 PM
trophybook trophybook is offline
Banned
 
Join Date: Jan 2010
Location: West of the 5th
Posts: 954
Default

Ain't going to be cheap. May aswell get line power. The diesel or gas will be ridiculous. 3 phase genny are not cheap
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -6. The time now is 05:40 AM.


Powered by vBulletin® Version 3.8.5
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.