Default Reznor Unit Heater Won't Light

I have a REznor unit heater that won't ignite in my garage.

I changed the diaphram and the venter motor. The venter motor was shot, the old one didn't turn on at all.

But it still doesn't ignite. The green light in the board blinks non stop calling for heat and the starts blinking twice.

WHat else could it be?
Reply With Quote
  #2  
Old 11-18-2012, 02:48 PM
Stu Stu is offline
 
Join Date: Apr 2010
Posts: 105
Default Reznor

Fan comes on?
Tries to lite? Can you hear it ticking?
Does it lite at all?
Reply With Quote
  #3  
Old 11-18-2012, 03:00 PM
Kokanee9's Avatar
Kokanee9 Kokanee9 is offline
 
Join Date: Feb 2011
Location: Calgary
Posts: 1,769
Default

I have a regular furnace in the garage that I had problems lighting for the first time. I had never had it going since I had bought the place.

First problem was that there was a second valve in the house that I didn't know about. Once I had found that, the second problem was that there was air in the line from the house all the way to the garage that needed to be purged out. Once that was accomplished, it ran fine.

Hope this helps.
__________________
Don't be a Skippy!

http://youtu.be/ZLDzPH-cBhw
Reply With Quote
  #4  
Old 11-18-2012, 03:00 PM
fishunter327's Avatar
fishunter327 fishunter327 is offline
 
Join Date: Oct 2012
Location: 65km south of Stoner
Posts: 643
Default

Quote:
Originally Posted by riden View Post
I have a REznor unit heater that won't ignite in my garage.

I changed the diaphram and the venter motor. The venter motor was shot, the old one didn't turn on at all.

But it still doesn't ignite. The green light in the board blinks non stop calling for heat and the starts blinking twice.

WHat else could it be?
not familier with that heater,but most gas units sequence of operation start with call for heat,combustion blower starts,pressure switch proves ,pilot(or )ignitor)fires ,proves pilot,main flame ignition.Because you have a led light blinking twice ,that is a code for a problem I would say,check the manual for what that indicates.These are somewhat general instructions so good luck.if you post the model # I can look the manual and get a better idea what kind of heater it is.
Reply With Quote
  #5  
Old 11-18-2012, 03:06 PM
riden riden is offline
 
Join Date: Sep 2011
Posts: 3,543
Default

Quote:
Originally Posted by fishunter327 View Post
not familier with that heater,but most gas units sequence of operation start with call for heat,combustion blower starts,pressure switch proves ,pilot(or )ignitor)fires ,proves pilot,main flame ignition.Because you have a led light blinking twice ,that is a code for a problem I would say,check the manual for what that indicates.These are somewhat general instructions so good luck.if you post the model # I can look the manual and get a better idea what kind of heater it is.
Two lights means pressure switch didn't prove. It never clicks.


If it isn't the venter motor or pressure switch, I don't know what it could be?
Reply With Quote
  #6  
Old 11-18-2012, 03:20 PM
Stu Stu is offline
 
Join Date: Apr 2010
Posts: 105
Default

Quote:
Originally Posted by riden View Post
Two lights means pressure switch didn't prove. It never clicks.


If it isn't the venter motor or pressure switch, I don't know what it could be?
Reply With Quote
  #7  
Old 11-18-2012, 03:24 PM
fishunter327's Avatar
fishunter327 fishunter327 is offline
 
Join Date: Oct 2012
Location: 65km south of Stoner
Posts: 643
Default

Quote:
Originally Posted by riden View Post
Two lights means pressure switch didn't prove. It never clicks.


If it isn't the venter motor or pressure switch, I don't know what it could be?
the pressure switch connected to combustion blower by 2 hoses ,am i correct for your model,make sure hoses are on correct location,check the little nipple the hose slips on ,these things get plugged with deposits and won,t let pressure switch get the vacuum it needs.suck and blow on the hose as well and get the pressure switch to operate,sometimes they get sticky from sitting over the summer
Reply With Quote
  #8  
Old 11-18-2012, 03:42 PM
riden riden is offline
 
Join Date: Sep 2011
Posts: 3,543
Default

Quote:
Originally Posted by fishunter327 View Post
the pressure switch connected to combustion blower by 2 hoses ,am i correct for your model,make sure hoses are on correct location,check the little nipple the hose slips on ,these things get plugged with deposits and won,t let pressure switch get the vacuum it needs.suck and blow on the hose as well and get the pressure switch to operate,sometimes they get sticky from sitting over the summer
I will try all these, but this is getting frustrating

Thanks
Reply With Quote
  #9  
Old 11-18-2012, 04:06 PM
fishunter327's Avatar
fishunter327 fishunter327 is offline
 
Join Date: Oct 2012
Location: 65km south of Stoner
Posts: 643
Default

Quote:
Originally Posted by riden View Post
I will try all these, but this is getting frustrating

Thanks
you can put a jumper wire on the 2 wires on the pressure switch to prove to yourself that this IS the issue.THIS IS ONLY FOR TROUBLE SHOOTING do not leave it there to fix the problem,you are bypassing a safety device.And then you figure out why it isn,t working or use a voltmeter to check for 24volts to ground on both sides of the switch.
Reply With Quote
  #10  
Old 11-18-2012, 04:10 PM
riden riden is offline
 
Join Date: Sep 2011
Posts: 3,543
Default

Success.

It was a build up in the nipple, my guess saw dust.

Thanks!
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -6. The time now is 07:55 PM.


Powered by vBulletin® Version 3.8.5
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.